Advanced disablement via keyswitch input
#1
All,
   We have an advanced panel with void detectors and remote leds (which due to the existing cable are not physically connected and it is all done by programming so detector x activates beacon y on the loop)

Testing is awkward as we have to leave beacons enabled so when we test void detectors ALL beacons operate not just the one we're testing. I've been told i can connect a keyswitch to one of the internal inputs to disable all main beacons and leave the detector void beacons enabled however i would also like this keyswitch to turn the panel buzzer off - any ideas how?

Also if i turn the internal keyswitch to isolate all sounders, relays and selected beacons can i then put the panel into walk test with sounders and use this to activate only the beacons i want to test? Or will the walk test with sounders override the keyswitch disablement and set the whole place into alarm,

Advanced weren't sure and advised me to try it...
Reply
#2
Panel buzzer can't be done, you can put it all into test and then put into commission mode which turns off buzzer.
Just fit keyswitch and assign to disablement group of your choosing then add any outputs you want.
Whistle Admit to nothing, deny everythingWhistle
Reply
#3
You don’t have to fit a key switch (which can be used by anyone) you can just use a link on the input pins if you go the disablement route or use the disable group menu

Or just untick the may walk test box on all outputs you don’t want operating  in walk test.
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Hochiki and Advanced mxpro5 panel dcarney 3 236 29-07-2020, 09:05 PM
Last Post: dcarney
  Xp95 I/O unit input earth fault Bero 8 481 15-07-2020, 03:34 PM
Last Post: Graeme
  Advanced mx4000 networking dcarney 8 1,128 24-06-2020, 03:08 PM
Last Post: davefiresafety
  Advanced loop card failure Mx5 Pro Dan 9 809 10-06-2020, 06:48 AM
Last Post: bob1
  Advanced mxpro 4 intermittent open circuit jordanjor 8 1,690 09-10-2019, 04:43 PM
Last Post: MD Martin
  EM Vents - Advanced MxPro5 Next4467 7 1,829 29-08-2019, 02:30 PM
Last Post: Next4467
  Advanced call point delays Bero 2 1,056 11-06-2019, 02:25 PM
Last Post: sparky999
  Advanced C&E Senator 10 3,133 15-04-2019, 10:49 PM
Last Post: Senator
  ems and advanced Advel Tech Support alonso 14 2,967 06-03-2019, 12:55 AM
Last Post: dubfireengineer
  Gent Vigi - Disablement Functions Dan 6 2,318 03-12-2018, 09:42 PM
Last Post: rudedog

Forum Jump:


Users browsing this thread: 1 Guest(s)