Servicing following a fire
#1
Just attended a site following a fire , its a conventional system with extensive smoke damage in some areas. I thought i had seen it in the BS , following a fire any contaminated automatic devices should be replaced, therefore I'm going to assume all devices in this area require replacement.I know its common sense but am i correct?
Reply
#2
There's a requirement for a special inspection following a fire but I can't see anything specific re replacing contaminated devices ....

As you say, it's common sense really ......
===============================
Some men aren't looking for anything logical. They can't be bought, bullied, reasoned, or negotiated with. Some men just want to watch the world burn.
Established 1985 - BAFE SP203 - Wireless Fire Alarm System Specialists
http://www.ctafire.co.uk
Reply
#3
46.4.5 Recommendations for inspection and test of the system following any fire
The following recommendations should be carried out as soon as possible after any fire.
a) Every manual call point, automatic fire detector and fire alarm device that might have been affected by the fire should be inspected and tested in
accordance with 45.4.
b) A visual examination and suitable tests should be carried out on any other part of the system that lies within the fire area and other areas affected by corrosive smoke from the fire and that might have been damaged by the fire (e.g. power supplies, control equipment and cable). Where there is evidence of damage, suitable action should be taken.
c) Circuits external to the CIE that could have been affected by the fire should be tested for correct operation.
d) On completion of the work, any defects found should be recorded in the system logbook, and the premises management should be notified accordingly.
www.fia.uk.com

Technical Manager FIA

All comments and views are mine own and may not reflect the views of FIA
Reply
#4
(10-04-2017, 02:52 PM)Will Lloyd Wrote: 46.4.5 Recommendations for inspection and test of the system following any fire
The following recommendations should be carried out as soon as possible after any fire.
a) Every manual call point, automatic fire detector and fire alarm device that might have been affected by the fire should be inspected and tested in
accordance with 45.4.
b) A visual examination and suitable tests should be carried out on any other part of the system that lies within the fire area and other areas affected by corrosive smoke from the fire and that might have been damaged by the fire (e.g. power supplies, control equipment and cable). Where there is evidence of damage, suitable action should be taken.
c) Circuits external to the CIE that could have been affected by the fire should be tested for correct operation.
d) On completion of the work, any defects found should be recorded in the system logbook, and the premises management should be notified accordingly.
 
Typical BS , it doesn't really identify the servicing responsibilities other than to test the devices for operation, on a conventional system that doesn't really identify whether the device has been contaminated. Going to apply the BS according to commonsense and replace all devices which may have been contaminated by smoke ingress.
Reply
#5
We recently had a fire and death in one of our buildings, system worked correctly thankfully.
I went in and inspected the system and documented all detectors in any area that had smoke residue evident ne replaced. Which was most of one side of the building.
We just ripped out the system as it was old and replaced the lot.
So yes, any smoke residue in the area, replace devices.
Bugger, I did isolate the dialer...didn't I?
Oops
Reply
#6
(10-04-2017, 04:09 PM)kevin hynes Wrote:
(10-04-2017, 02:52 PM)Will Lloyd Wrote: 46.4.5 Recommendations for inspection and test of the system following any fire
The following recommendations should be carried out as soon as possible after any fire.
a) Every manual call point, automatic fire detector and fire alarm device that might have been affected by the fire should be inspected and tested in
accordance with 45.4.
b) A visual examination and suitable tests should be carried out on any other part of the system that lies within the fire area and other areas affected by corrosive smoke from the fire and that might have been damaged by the fire (e.g. power supplies, control equipment and cable). Where there is evidence of damage, suitable action should be taken.
c) Circuits external to the CIE that could have been affected by the fire should be tested for correct operation.
d) On completion of the work, any defects found should be recorded in the system logbook, and the premises management should be notified accordingly.
 
Typical BS , it doesn't really identify the servicing responsibilities other than to test the devices for operation, on a conventional system that doesn't really identify whether the device has been contaminated. Going to apply the BS according to commonsense and replace all devices which may have been contaminated by smoke ingress.

I would, or certainly recommend it, there is a high probability that either the detectors are going to be less sensitive, or, more likely to be prone to unwanted alarms, so definitely recommend replacements.
30 years in the fire industry, BAFE accredited, every FIA & BFPSA course, and still learning, but sparky knows it all!
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Fire alarm maintenance and sprinklers rtfm 1 107 22-01-2020, 12:02 PM
Last Post: Monkeh
  risk assessment AFTER fire alarm systems split alonso 3 1,002 22-11-2019, 07:10 PM
Last Post: Marian Prala
  Cable requirements for fire alarm outputs Dan 9 673 19-10-2019, 06:18 PM
Last Post: Graeme
  legal period for keeping fire alarm records in logbook alonso 7 1,402 23-07-2019, 05:27 PM
Last Post: Graeme
  Fire doors closing not immediate luggsey 3 664 02-05-2019, 02:53 PM
Last Post: luggsey
  New system servicing /takeovers KKGMC 21 2,800 24-03-2019, 12:12 PM
Last Post: Graeme
  Linking a Fire Alarm to a Sprinkler System Dan 5 941 22-02-2019, 10:40 PM
Last Post: Graeme
  Replacement of cabling to fire-resisting rtfm 7 764 15-02-2019, 08:41 PM
Last Post: AnthonyB
  fire relay operating 3 other relays to operate shutdowns and fire pagers alonso 6 2,038 26-11-2018, 11:56 PM
Last Post: sparky999
  how dedicated a dedicated fire alarm supply? alonso 21 2,826 19-10-2018, 08:01 PM
Last Post: Trickle Charge

Forum Jump:


Users browsing this thread: 1 Guest(s)