Kentec integral sounder mode
#1
Lads just wondering has anyone set this type of setup on a large enough system ( 15 panels networked) They are student accommodation apartments so if a device activates in that apartment the sounder in that apartment operate and after 6 mins if it's not reset it evacuated that block.
If a device in a common hallway or stairs activates it starts the 6 min delay and then evacuated all of that block. There's approx 28 apartments per block.
Reply
#2
Done simular not on network but it won't be much different on network, just some C&E across the network.
Aint gonna be straightforward on Kentec - a lot C&E lines and some limitations you will have and some silly setups to overcome the C&E limitations. If you had Advanced, it would be much quicker to do the C&E.
Reply
#3
(17-05-2017, 06:05 PM)alex88 Wrote: Done simular not on network but it won't be much different on network, just some C&E across the network.
Aint gonna be straightforward on Kentec - a lot C&E lines and some limitations you will have and some silly setups to overcome the C&E limitations. If you had Advanced, it would be much quicker to do the C&E.

We had Advanced ordered for the job (only use kentec for non networked systems now due to their limitations of anything slightly complex) but client is insisting on kentec as they have it on other sites.
Was thinking the only way around it was using the fire and alarm contacts and putting a delay on them and having no delay on the sounders and outputs and letting the relays use the delay, not a fan of depending on relays only to activate the sounders at all though.
Reply
#4
Done it on EMS system using the above method mate.

Lot of messing about but worked out in the end.
Reply
#5
I wouldn't mind to set up few lines for you just to see if we are on same page. Haven't done anything complex lately and don't wanna get rusty lol
Reply
#6
(17-05-2017, 11:41 PM)alex88 Wrote: I wouldn't mind to set up few lines for you just to see if we are on same page. Haven't done anything complex lately and don't wanna get rusty lol

PM me your email Alex, I'll send you over the file when I get the first block programmed.
Reply
#7
I hope my email from last night didn't go to spam
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Kentec software corrupting files Stevem 19 441 04-01-2018, 10:50 AM
Last Post: alex88
  Ems firecell and kentec syncro questions alonso 27 910 14-12-2017, 09:21 PM
Last Post: bob1
  Kentec Syncro With Graphics JohnH 7 397 23-11-2017, 08:16 PM
Last Post: Royce44
  Kentec Syncro Peter Stanton 21 1,398 06-11-2017, 05:31 PM
Last Post: bob1
  Kentec protocol bob1 10 824 05-10-2017, 10:33 AM
Last Post: bob1
  Kentec Syncro Alex Milner 51 5,767 05-08-2017, 09:43 AM
Last Post: Alex Milner
  Kentec panel with keypad unimatrix1066 25 4,163 27-03-2017, 09:44 AM
Last Post: unimatrix1066
  Kentec Solo and software Danno 32 23,594 28-11-2016, 12:11 AM
Last Post: sparky999
  Morley zx5se day delay mode & isolate-key switches Clarkie 5 1,424 26-11-2016, 07:28 PM
Last Post: Monkeh
  1amp sounder cct unimatrix1066 24 5,854 14-10-2016, 06:34 PM
Last Post: martinh1234

Forum Jump:


Users browsing this thread: 1 Guest(s)