High resistance loop advanced mx pro 5
#11
(04-05-2018, 09:56 AM)Graeme Wrote: as mentioned - go to commission - next menu - EN54-13 and tick on the tick.

or set it up based on your loop calculations with the Config SW
All posts are of my own opinion and knowledge and do not reflect the views of the Company I work for.
Reply
#12
(04-05-2018, 07:45 AM)Trickle Charge Wrote: What the diff between a mx4 and a mx5. Sorry if this a dumb question but I only use Kentech.

Basic features not much.

 More advanced features- quite a lot 

2000 network zones instead of 1000, 200 network sectors instead of 50 more false alarm management, better logging, fully en54 compliant. Fully supports Apollo voice sounders to name a few. Still can’t share network zones though but still better than Kentec imho

I don’t think the pro 4 is being uodated any more either
Reply
#13
Built in 20 zone led card too
Reply
#14
(04-05-2018, 07:45 AM)Trickle Charge Wrote: What the diff between a mx4 and a mx5. Sorry if this a dumb question but I only use Kentech.

For a start mx5 has 2000 zones and there is more in the menus and supports newer devices
Peter Robinson




07889 038650

Reply
#15
(02-05-2018, 10:22 PM)dcarney Wrote: With a new install surely the loop should not have high resistance , will switching off this cause problems later such as intermittent open circuit fault if there is a loose connection ? Had a intermittent open circuit fault on previous system and it was a loose connection in loop siren that was on drywall and when the door of office was banged it would throw up a fault , never  a problem when no one was around , tightening connection , no fault since.

Turn EN54 off :)
Peter Robinson




07889 038650

Reply
#16
(04-05-2018, 01:15 PM)Mr C Wrote:
(04-05-2018, 07:45 AM)Trickle Charge Wrote: What the diff between a mx4 and a mx5. Sorry if this a dumb question but I only use Kentech.

Basic features not much.

 More advanced features- quite a lot 

2000 network zones instead of 1000, 200 network sectors instead of 50 more false alarm management, better logging, fully en54 compliant. Fully supports Apollo voice sounders to name a few. Still can’t share network zones though but still better than Kentec imho

I don’t think the pro 4 is being uodated any more either
But best feature is that "Disable all Outputs" works across the network and not just limited to the panel you're on .......  Biggrin
===============================
Some men aren't looking for anything logical. They can't be bought, bullied, reasoned, or negotiated with. Some men just want to watch the world burn.
Established 1985 - BAFE SP203 - Wireless Fire Alarm System Specialists
http://www.ctafire.co.uk
Reply
#17
(04-05-2018, 04:29 PM)ESP Wrote:
(04-05-2018, 01:15 PM)Mr C Wrote:
(04-05-2018, 07:45 AM)Trickle Charge Wrote: What the diff between a mx4 and a mx5. Sorry if this a dumb question but I only use Kentech.

Basic features not much.

 More advanced features- quite a lot 

2000 network zones instead of 1000, 200 network sectors instead of 50 more false alarm management, better logging, fully en54 compliant. Fully supports Apollo voice sounders to name a few. Still can’t share network zones though but still better than Kentec imho

I don’t think the pro 4 is being uodated any more either
But best feature is that "Disable all Outputs" works across the network and not just limited to the panel you're on .......  Biggrin

Easy enough to set up one of the function buttons for group disable on an mxpro 4 though it's a bit time consuming initially
Reply
#18
(05-05-2018, 02:36 AM)Monkeh Wrote:
(04-05-2018, 04:29 PM)ESP Wrote:
(04-05-2018, 01:15 PM)Mr C Wrote:
(04-05-2018, 07:45 AM)Trickle Charge Wrote: What the diff between a mx4 and a mx5. Sorry if this a dumb question but I only use Kentech.

Basic features not much.

 More advanced features- quite a lot 

2000 network zones instead of 1000, 200 network sectors instead of 50 more false alarm management, better logging, fully en54 compliant. Fully supports Apollo voice sounders to name a few. Still can’t share network zones though but still better than Kentec imho

I don’t think the pro 4 is being uodated any more either
But best feature is that "Disable all Outputs" works across the network and not just limited to the panel you're on .......  Biggrin

Easy enough to set up one of the function buttons for group disable on an mxpro 4 though it's a bit time consuming initially

But far nicer to have a function of the control panel do what it says on the tin than rely on the previous engineer adding the last sounder he added to the disablement group ..........
===============================
Some men aren't looking for anything logical. They can't be bought, bullied, reasoned, or negotiated with. Some men just want to watch the world burn.
Established 1985 - BAFE SP203 - Wireless Fire Alarm System Specialists
http://www.ctafire.co.uk
Reply
#19
True enough
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Hi Resistance on loop dcarney 4 572 11-12-2019, 01:01 AM
Last Post: Dan
  Advanced mxpro 4 intermittent open circuit jordanjor 8 946 09-10-2019, 04:43 PM
Last Post: MD Martin
  Kentec Synchro hochiki Loop Explorer Software jmsa7 3 2,868 05-10-2019, 09:17 PM
Last Post: Ali Sulaiman
  EM Vents - Advanced MxPro5 Next4467 7 1,188 29-08-2019, 02:30 PM
Last Post: Next4467
  Advanced disablement via keyswitch input alonso 2 612 30-07-2019, 06:50 PM
Last Post: Mr C
  Advanced call point delays Bero 2 700 11-06-2019, 02:25 PM
Last Post: sparky999
  Advanced C&E Senator 10 2,184 15-04-2019, 10:49 PM
Last Post: Senator
  SURGE PROTECTION ON LOOP Pro Metheus 2 702 10-04-2019, 09:25 PM
Last Post: Pro Metheus
  ems and advanced Advel Tech Support alonso 14 2,065 06-03-2019, 12:55 AM
Last Post: dubfireengineer
  Kentec syncro as loop fault dcarney 13 2,722 23-02-2019, 10:58 PM
Last Post: Dan

Forum Jump:


Users browsing this thread: 1 Guest(s)