Panel change
#1
Thoughts please
Changing a panel and adding a few devices.
The client wants to leave all the old devices as they are but in certain areas they don't conform.
Would you just write the variations on the certificate or insist the building is brought up to standards.
Thanks in advance
Any views expressed are that of my own not my company!Exclamation
Reply
#2
Variation cert, get customer to sign it. You have given the recommendations, they have signed to say they have acknowledged it. It becomes their responsibility.
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#3
As Dan says issue a variation cert with your recommendations and get the customer to sign it
Peter Robinson




07889 038650

Reply