Gent Vigi - Disablement Functions
#1
Just after a bit of advice!

I'm currently covering call out for a mate, he looks after a stadium that has a Gent Vigi consisting of 3 panels. The stadium events manager called me this afternoon and asked if I could attend tomorrow night to disable some zones on the system as they will be using smoke machines. I'm rusty with Gent, not worked on it for quite some time.

If I remember correctly, will I need to disable the zones on each panel? I seem to remember disablements are only local, not issued over the network.

Also, does anyone know the menu sequence for accessing zone disablements? I don't want to turn up tomorrow looking like an idiot if I can help it!  Biggrin
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#2
Control disable zone


Disablements can go cross network but only if an input on one panel is programmed to disable something on another panel. 
If you're disabling zones you'll need to do it on each panel.
Reply
#3
Cheers Monkeh!
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#4
(26-10-2018, 06:21 PM)Dan Wrote: Cheers Monkeh!

Back to this...

Iv been given some information from a gent engineer on how to put these Vigi's in one man test, just in case I ever need to service one of these in the future! Iv typed up a document for 2 scenarios

* to carry out a one man test with all outputs, panel buzzer and sounders isolated
* to carry out a one man test with sounders and outputs enabled. 


.pdf   Gent Isolation.pdf (Size: 136.74 KB / Downloads: 215)

Does the info I have typed up look correct? 
Anything I should change or add to it?

I will put a final copy up on this thread in case anyone as sh**t as me with Gent finds this document useful  Biggrin
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#5
the only things I'd say are:

you can disable comms at card x (6 for me) instead of disabling at every panel in a network and then just test the panel you're working on (obviously be careful not to stray!)

and some panels use 'commission' instead of walk test as a term. they mean the same thing.
Reply
#6
Downloaded it , nice one Dan.

Never worked on Gent Vigi but may come in handy one day.
Reply
#7
On a vigilon panel if its in test mode, it doesn't issue signals over the network they are always local, and as alonso said you only need to disable comms on the panel you are working on.
There shouldn't be any real need to disable command builds as these shouldn't be priority fire events.

most important thing to be aware of is even with all outputs isolated if you press sound alarms the alarms will go off!
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  gent network fault alonso 1 441 30-10-2019, 09:59 PM
Last Post: Harrysu
  Advanced disablement via keyswitch input alonso 2 549 30-07-2019, 06:50 PM
Last Post: Mr C
  gent xen conventional bases alonso 1 455 24-07-2019, 10:12 PM
Last Post: luggsey
Exclamation Gent Vigilon Engineer Reset matthewhughes1 7 2,109 31-01-2019, 04:54 AM
Last Post: douglas docherty
Rolleyes Need Help with GENT CommTool amj 12 3,233 30-01-2019, 11:45 PM
Last Post: Adi
  URGENT GENT VIGILON matthewhughes1 4 1,287 26-01-2019, 07:43 PM
Last Post: Harrysu
  Gent Loop matthewhughes1 2 1,194 23-01-2019, 05:52 PM
Last Post: atherton1930
  Gent Tone & Message Numbers matthewhughes1 0 512 22-01-2019, 11:44 PM
Last Post: matthewhughes1
  Gent Nano change device type Bero 2 839 27-11-2018, 11:17 AM
Last Post: Bero
  gent silence and sound alarm events in an empty building alonso 10 2,176 26-10-2018, 07:03 PM
Last Post: Harni

Forum Jump:


Users browsing this thread: 1 Guest(s)