Wagner
#1
Hi all

I'm servicing a system at the minute with a load of these. It seems some of them have the fault latching and some have them non latching.

They are all monitored through an i/o and all have 24v on reset applied.

I would have thought non latching but with the 24v reset applied anyway does it make any difference?

Not overly familiar with these so reaching out for some guidance.

Thanks in advance
Reply
#2
https://www.manualslib.com/manual/123349...tanus.html

Here is a link to a manual not sure if this is what you are looking for
Peter Robinson




07889 038650

Reply
#3
Afternoon, the fault latch for these is set by dip switch 9 on the sensor module, set to latch by default. The fire latch is disabled by connecting a 24v supply to the reset terminals.

Hope this helps.
Reply
#4
(04-02-2019, 04:25 PM)Rubble1952 Wrote: Afternoon, the fault latch for these is set by dip switch 9 on the sensor module, set to latch by default. The fire latch is disabled by connecting a 24v supply to the reset terminals.

Hope this helps.

Thanks.
But how do you clear a fault then if you use the default setting ie latching I thought the 24v supply to reset would reset fault condition also.
Reply