Extinguisher agent question
#1
I'm 100% alarms but someone asked me this question and I didn't actually know the answer so here it goes

I know the basics of an extended service, why they're carried out etc but do the AFFF foam and ABC powder agents have a limited life ? IE if no extended service was carried out for 10 years, would the effectiveness of the agent be less effective against a fire ?
Reply
#2
Foam compounds do degrade over time, particularly in solution, although not as bad as the older protein based compounds. This can affect efficacy particularly on Class B fires.

As for powder, less clear - in the US equivalent of an ES (at 6 years) they will use a closed recycling system to discharge the powder into and if still free flowing they will put it back in.
Anthony Buck
Fire Safety Technical Lead @ BAFE SP205 accredited company
Extinguisher specialist

http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
http://www.linkedin.com/pub/anthony-buck/22/957/36b
Reply
#3
Thanks Anthony you're knowledge never fails to impress!
Reply
#4
(15-07-2019, 05:44 PM)AnthonyB Wrote: Foam compounds do degrade over time, particularly in solution, although not as bad as the older protein based compounds. This can affect efficacy particularly on Class B fires.

As for powder, less clear - in the US equivalent of an ES (at 6 years) they will use a closed recycling system to discharge the powder into and if still free flowing they will put it back in.

picking up on your impressive knowledge, would it not be a more cost effect solution to replace them as they might also require a pressure test ?.

bob
Reply
#5
Unlike the US, there is no requirement to pressure test types other than CO2 unless being repainted/refurbished.

Powder became cheaper to replace new when the Chinese stuff started to appear at the beginning of the century as you are supposed to use new powder here, not recycle it, so the few quid price difference between powder sacks and a new unit wasn't worth refilling, especially with the mess and the risk of leaks if you hadn't thoroughly cleaned the spindle, etc.

A few fire extinguisher firms still refill and discharge test wets as the cost difference is still worth it.
Anthony Buck
Fire Safety Technical Lead @ BAFE SP205 accredited company
Extinguisher specialist

http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
http://www.linkedin.com/pub/anthony-buck/22/957/36b
Reply
#6
I don't. Just so much easier replacing every 5 years.
Reply
#7
I suppose it’s down to quantity and facilities.

The cost savings made by refilling will be lost elsewhere, such as having a large unit to store bottles and work from and staff to pay to actually do the discharge and refill. You would need to be turning around a huge number to make it worthwhile I would expect?
www.ajfire.co.uk

"Independent BAFE Accredited Fire Protection Specialists"

- SP203-1; FDA Maintenance; 
- SP205-1; Life Safety Fire Risk Assessment
- Members of the Fire Industry Association (FIA)
- SafeContractor Approved


Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Silver extinguisher alonso 2 423 09-07-2019, 11:49 PM
Last Post: Tilly
  BS5306-3:2017 Extinguisher Servicing AnthonyB 12 5,991 17-11-2017, 08:15 PM
Last Post: Messy
  Old minimax extinguisher (1932) firemonkey 5 3,267 22-04-2017, 10:50 PM
Last Post: AnthonyB
  Extinguisher maintenance contract template? Danno 1 1,524 09-02-2017, 10:00 PM
Last Post: Tilly
  Free fire extinguisher servicing Will1989 9 5,483 14-07-2016, 08:10 AM
Last Post: Tilly
  Fire extinguisher servicing Bristol Leolion2177 0 1,874 27-10-2014, 10:18 AM
Last Post: Leolion2177
  Fire Extinguisher Service Van Kitout Leolion2177 5 4,052 11-09-2014, 06:47 PM
Last Post: jmeservices
  Urgent - Anyone cover Falkirk for extinguisher servicing Leolion2177 2 2,872 07-06-2014, 03:42 PM
Last Post: Leolion2177
  Extinguisher toolkit pieman 3 3,677 31-05-2014, 12:39 AM
Last Post: pieman
  Self maintenance extinguisher Bob Transformer 18 17,200 11-02-2014, 08:16 PM
Last Post: AnthonyB

Forum Jump:


Users browsing this thread: 1 Guest(s)