JSB Firedex FX2200 test mode
#1
We have, what I assume is, a Firedex FX2200 (the one with five yellow buttons, not four) where apparently in detector test mode the first three detectors tested are okay, the panel silences and resets after each one, so move onto the next. Then on the fourth detector whilst in test the panel goes into fault, gives up and the zones needs depowering and repowering.

I can't see anything looking at the manuals, only that the 2200 has a one-shot test mode (so I assumed it would come out of test after the first fire has been received) but then I have another Coopers manual for what appears to be the same panel, and whilst it states one man test mode it makes no mention of it being one shot.

I'd assume as our engineers come across these panels fairly regularly this one is sticking out as having something wrong with it, and the others we maintain we can merrily test more than three detectors and all is okay.

This is happening on two of the zones.

When it happens the voltage on the zone drops to around 2 volts, and when zone + or - is removed it comes back up to 24v again.

It's possible that the site does not have its original control panel so there could be a compatibility issue with the wiring/detection. It's not a dead-short callpoint as the devices being tested are automatic smoke or heat detectors. It's presumably not current draw in alarm on the zone from multiple detectors as the panel has silenced and reset before the next is tested - or is it - does the panel need longer between detector tests for the zone to 'recover'?
Reply
#2
The Customer test is one shot but the Engineer walk test isn't.

The code is usually inside the front cover .
All posts are of my own opinion and knowledge and do not reflect the views of the Company I work for.
Reply
#3
Thanks, that explains the discrepancy in what I'm reading in the manuals. The maintenance engineer is probably aware of that on site.

No mention though in the manual that only a limited number of detectors can be tested though?
Reply
#4
I might be wrong, but I seem to remember the Cooper versions work a bit differently, I think their boards are different but they use the same housing as JSB.
Nothing is foolproof to a sufficiently talented fool...   24

Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Tyco MX - Detectors Failing Self Test? aeg 3 666 12-06-2019, 05:58 PM
Last Post: SFSS
  Ziton zp3 walk test dcarney 9 1,546 16-02-2019, 01:57 PM
Last Post: Monkeh
  Advanced diagnostic mode logs luggsey 22 6,797 09-02-2018, 12:12 AM
Last Post: sparky999
  Kentec integral sounder mode dubfireengineer 6 4,115 20-05-2017, 12:20 PM
Last Post: alex88
  Morley zx5se day delay mode & isolate-key switches Clarkie 5 3,920 26-11-2016, 07:28 PM
Last Post: Monkeh
  morley & system sensor sounders keep sounding after weekly test alonso 29 21,670 28-09-2016, 11:29 AM
Last Post: bob1
  Firedex FX2202 Weatherproof sounders? Leolion2177 3 2,600 28-05-2016, 01:14 PM
Last Post: Leolion2177
  Fire alarm weekly test reminder John 20 10,363 22-04-2016, 10:51 PM
Last Post: Monkeh
  minerva 80 relay test alonso 2 2,395 29-03-2016, 04:52 PM
Last Post: alonso
  Firedex 2208 Bi-Wire ecgservices 10 7,599 26-08-2015, 01:01 AM
Last Post: tc(two cup)

Forum Jump:


Users browsing this thread: 1 Guest(s)