Hi all
I have a client that has an analogue protec panel with an interface that was signalling another site, they no longer require this signalling so i need to disconnect the input and output from the interface, the problem is i cant find out what the EOL value needs to be for the input. I have googled it but cant see anything.
Any help would be great.
   
Reply
#2
10k I think
Reply
#3
(25-07-2019, 04:16 PM)COMM ENGINEER Wrote: 10k I think

Thanks
Reply
#4
If you want someone to get downloads of the system let me know, I can work on the protec panels
*Hits call point*... "we are on test aren't we?"... Whoops 
Reply
#5
47k is the Input resistance

And it looks like theres already one in the interface, (bottom left)
Blue resistor
Reply
#6
(25-07-2019, 07:54 PM)RMC Wrote: 47k is the Input resistance

And it looks like theres already one in the interface, (bottom left)
Blue resistor

Hi
Yes your right, i went back early this morning and saw that resistor hanging out of the relay connections only connected on one side, im guessing so it wasnt lost.
I put my meter across and it is 47K. Thanks for your help.
Reply
#7
(25-07-2019, 05:28 PM)Harrysu Wrote: If you want someone to get downloads of the system let me know, I can work on the protec panels

Hi
I my do as i'm recommending to the client to replace the system with an open protocol system so a download to identify all devices would be helpful, what area are you in? The system is in South Essex.
Reply
#8
I’m in Birmingham but cover all areas
*Hits call point*... "we are on test aren't we?"... Whoops 
Reply
#9
(26-07-2019, 02:48 PM)Harrysu Wrote: I’m in Birmingham but cover all areas

Will bear that in mind if they want to go ahead with a change out.
Reply
#10
(26-07-2019, 04:09 PM)Next4467 Wrote:
(26-07-2019, 02:48 PM)Harrysu Wrote: I’m in Birmingham but cover all areas

Will bear that in mind if they want to go ahead with a change out.

Just change the panel to a 6500
It will run both 6000 & 6000 plus devices & is open
Also fits into the existing enclosure 

No need change all the devices
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Protec Labels mr ab 4 511 03-03-2019, 10:23 AM
Last Post: mr ab
  Protec 5200 Fire98 6 1,020 04-11-2018, 03:40 PM
Last Post: hothead
  Protec rossk 3 1,080 10-08-2018, 09:31 AM
Last Post: 11aliadnan
  BS7273-4 compliant interface to fire alarm panel CaptainSlog 33 8,951 16-01-2018, 02:12 AM
Last Post: CaptainSlog
  BS7273-4 fail safe interface analysis CaptainSlog 11 3,169 14-01-2018, 12:10 AM
Last Post: CaptainSlog
  Protec 3100eol unimatrix1066 2 1,169 22-11-2017, 11:12 PM
Last Post: unimatrix1066
  Protec 6300 sbowden42 12 6,216 19-10-2017, 11:21 PM
Last Post: sbowden42
  Protec Print Outs Dean_Clough 14 8,753 17-06-2016, 08:03 AM
Last Post: Tilly
  Protec AN95 UKNerd 31 21,186 09-12-2015, 11:52 PM
Last Post: alonso
  protec 5200panel unimatrix1066 21 16,648 04-12-2015, 12:11 AM
Last Post: Garsec

Forum Jump:


Users browsing this thread: 1 Guest(s)