Thread Rating:
  • 0 Vote(s) - 0 Average
  • 1
  • 2
  • 3
  • 4
  • 5
Daily inspection
#1
Hello all :-)

I assume that the CIE on a part 6 grade A system needs a daily inspection the same as a part 1 system. 

I can't seem to find anything in the part 6 regs to confirm this though?

Is anyone able to point me in the right direction as my eyes are going funny trawling through this book  Biggrin

Cheers
Reply
#2
its in clause 47 of part 1 but not really spelled out in part 6 there is a weekly test for grade A
and the daily check is just to see that the fault light isn't on and the power supply is healthy as all panels that i'm aware of have fault buzzers its not that important anymore
www.fia.uk.com

Technical Manager FIA

All comments and views are mine own and may not reflect the views of FIA
Reply
#3
unless someone else has muted it
All posts are of my own opinion and knowledge and do not reflect the views of the Company I work for.
Reply
#4
(08-09-2019, 09:21 PM)Graeme Wrote: unless someone else has muted it

The number of systems we go to service, usually in flats, that have been silenced and left in fire condition is astounding! Its a daily occurrence. 
Try getting owners to upgrade to a mixed system. No chance!
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  MCP's in a garage inspection pit alonso 11 1,661 28-08-2019, 08:23 PM
Last Post: Tilly
  fire alarm and extinguisher inspection reports jamiejwarner 5 5,240 28-11-2012, 05:51 PM
Last Post: Martin

Forum Jump:


Users browsing this thread: 1 Guest(s)