Still Problems with Sprinklers.
#1
Morning, 

We are still looking for a cheaper alternative to a pump to stop mains fluctuations setting off the fire alarm.
Currently when emptying and refilling the system, any subsequent mains pressure increase sets off the alarm, usually at 2am on a sunday morning.

I have had a suggestion that a small bore pipe fitted each side of the clapper to equalize pressure would be an alternative to the pump.

Is this correct?

Would anyone be willing to do this do you think?

Thanks.
Reply
#2
Have you adjusted the delay on the flow switch? Set a input delay up on each flow switch monitor
Reply
#3
We used to get trouble with air bubbles movi g around causing this, would check for that.
Bugger, I did isolate the dialer...didn't I?
Oops
Reply
#4
Agree with Royce. Stick a delay on the input to fire panel. Flow switches should have them inbuilt
Reply
#5
Thanks, is there anyone around Manchester that could do it?
Reply
#6
(16-10-2019, 07:19 AM)Chris12345 Wrote: Thanks, is there anyone around Manchester that could do it?

Chris I'm guessing you are the Building Manager ? 

Do you not have an incumbent fire alarm system service company - they should be able to handle it. 

If not who ever does the work would need to know the make and model of the fire alarm system ?
===============================
Some men aren't looking for anything logical. They can't be bought, bullied, reasoned, or negotiated with. Some men just want to watch the world burn.
Established 1985 - BAFE SP203 - Wireless Fire Alarm System Specialists
http://www.ctafire.co.uk
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Code of Practice for Installation of Sprinklers in Schools admin 0 2,542 22-03-2011, 09:39 PM
Last Post: admin
  Sprinklers in Dwellings douglas docherty 0 2,533 21-03-2010, 12:35 PM
Last Post: douglas docherty
  Types of sprinklers AFFINITY 0 2,249 19-04-2008, 06:53 PM
Last Post: AFFINITY
  How sprinklers work AFFINITY 0 2,275 19-04-2008, 06:52 PM
Last Post: AFFINITY
  At what height do sprinklers become ineffective? Guest 1 3,758 19-04-2008, 06:49 PM
Last Post: AFFINITY

Forum Jump:


Users browsing this thread: 1 Guest(s)