kentec series 6000
#1
called out to a series 6000 kentec panel tonight on a fault condition. the panel displaying
 program memory fault- ROM checksum.
anyone had this problem and know how to fix, any help would be good 
 many thanks
Reply
#2
Rom checksum usually means something has unexpectedly changed in the panels memory. If it was me, I would take a download on the laptop, briefly check the programming over to make sure it's intact then upload it back into the panel. I'm not a massive fan of Kentec so I don't deal with them much. Someone on here may have some knowledge about it.
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#3
just had kentec on the phone and they seem to think the batteries are the issue. if the batteries are pulling to much current as a result of them not being able to charge correctly (still over 65% capacity) then this can cause the rom check sum fault. batteries replaced and system running normally now. will update if anything changes.
Reply
#4
(16-10-2019, 11:56 AM)Tony Wrote: just had kentec on the phone and they seem to think the batteries are the issue. if the batteries are pulling to much current as a result of them not being able to charge correctly (still over 65% capacity) then this can cause the rom check sum fault. batteries replaced and system running normally now. will update if anything changes.

Weird!

Explanation? = kentec!!!
Reply
#5
(16-10-2019, 01:07 PM)Salonso Wrote:
(16-10-2019, 11:56 AM)Tony Wrote: just had kentec on the phone and they seem to think the batteries are the issue. if the batteries are pulling to much current as a result of them not being able to charge correctly (still over 65% capacity) then this can cause the rom check sum fault. batteries replaced and system running normally now. will update if anything changes.

Weird!

Explanation? = kentec!!!

Ha ha I was thinking exactly the same!!
Reply
#6
(16-10-2019, 02:03 PM)Mr C Wrote:
(16-10-2019, 01:07 PM)Salonso Wrote:
(16-10-2019, 11:56 AM)Tony Wrote: just had kentec on the phone and they seem to think the batteries are the issue. if the batteries are pulling to much current as a result of them not being able to charge correctly (still over 65% capacity) then this can cause the rom check sum fault. batteries replaced and system running normally now. will update if anything changes.

Weird!

Explanation? = kentec!!!

Ha ha I was thinking exactly the same!!

WTF ???? 

First time I've hear that one! 

We've had similar and always turned out to be a processor issue - goes away and returns more and more frequently. 

Normally end up changing the door ..........
===============================
Some men aren't looking for anything logical. They can't be bought, bullied, reasoned, or negotiated with. Some men just want to watch the world burn.
Established 1985 - BAFE SP203 - Wireless Fire Alarm System Specialists
http://www.ctafire.co.uk
Reply
#7
so just an update on the problem with kentac series 600 panel showing "program memory fault- ROM checksum". as kentec suggested possible issue with batteries and/or charger well it's been 12 days now since changing the batteries and charger. viewed the panel this morning and all is well no faults no "program memory fault- ROM checksum" fingures crossed i wont have to use the new 2 loop panel i bought
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Kentec Sigma XT+ (3 Area) Triple 1 464 06-06-2020, 11:08 PM
Last Post: Royce44
  hochiki and kentec addressing alonso 9 2,190 15-10-2019, 12:30 PM
Last Post: alonso
  Kentec Synchro hochiki Loop Explorer Software jmsa7 3 3,832 05-10-2019, 09:17 PM
Last Post: Ali Sulaiman
  Kentec syncro as loop fault dcarney 13 4,138 23-02-2019, 10:58 PM
Last Post: Dan
  Apollo series 30 dcarney 6 2,082 27-11-2018, 12:15 PM
Last Post: Tilly
  Kentec - Remote PSU Advice Needed yangi19 6 2,556 23-11-2018, 08:16 PM
Last Post: yangi19
  Kentec software corrupting files Stevem 34 17,062 22-11-2018, 09:57 PM
Last Post: yangi19
  Kentec bi wire bob1 12 4,262 30-06-2018, 04:54 PM
Last Post: John
  Kentec syncro psu 3 pin green connectord alonso 3 2,273 25-01-2018, 08:36 PM
Last Post: Tilly
  Ems firecell and kentec syncro questions alonso 27 11,744 14-12-2017, 09:21 PM
Last Post: bob1

Forum Jump:


Users browsing this thread: 1 Guest(s)