Ctec conventional sounder issue
#1
Got a site which the sounders intermittently sound for a few seconds (think class change) no panel faults or fires reported 
We've already changed the panel about a year ago and was ok until now! Changed the sounders this week - was ok again for a couple of days but started again this morning.

Tech have no idea - anyone had anything like this before ? Cabling is all existing and done years ago by others so could be picking up induced ac from somewhere I'm guessing
Reply
#2
That's what I have experienced in the past from induced voltages from other services, especially if the zone is sharing the same routes as other services. There are a few options, re-run the wiring (which isn't always possible) or I have suggested to a couple of guys to fit Ferrites at the beginning of the affected circuits. Don't know if that worked because they never came back to me.
Wozza Apollo Tech
Reply
#3
I had this once and It took me ages but I eventually found it to be a cable fault.

It was an FP200 4-core that didn't have a big enough check in the joist and when someone walked over it , the sounders went.

The thing that took so long was finding a pattern and I found it was when the rather large Lady went on a break - No one else was heavy enough to flatten the cable - lol
All posts are of my own opinion and knowledge and do not reflect the views of the Company I work for.
Reply
#4
Fatties get the blame for everything ffs
Reply
#5
It's ok Monkeh, it's ok.


...do you want a shoulder to cry on?
Reply
#6
Have you checked the current being drawn from all sounder circuits? I know CFPs only have one sounder output source and its quite limited in terms of how much current it can handle.
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#7
Had this exact issue, sounder pulsing weirdly. When I removed just the grey core on an swa cable feeding the class change it stopped. Replaced the cable and no issues since
Reply
#8
(25-10-2019, 09:22 PM)Buggy Wrote: It's ok Monkeh, it's ok.


...do you want a shoulder to cry on?

Just had a sausage and bacon bap so I'm fine now .
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  apollo io issue dcarney 1 196 10-09-2020, 08:49 PM
Last Post: Monkeh
  Notifier Conventional Panels designguru 4 779 12-03-2020, 12:46 PM
Last Post: Monkeh
  2 Wire ADT Sounder. Chris12345 4 1,063 29-11-2019, 11:18 PM
Last Post: SFSS
  CTEC CFP and XP95 Interface dazmisiak 3 1,108 28-08-2019, 05:41 PM
Last Post: Dan
  gent xen conventional bases alonso 1 884 24-07-2019, 10:12 PM
Last Post: luggsey
  4 zone, 4 sounder outputs... Tilly 12 3,077 29-06-2019, 04:35 PM
Last Post: advancefireyork
  Apollo discovery sounder bases channelFS 1 1,244 26-01-2019, 07:19 PM
Last Post: Mr C
  Apollo xp95 sounder base faulty dcarney 20 5,326 02-01-2019, 12:43 PM
Last Post: wozzer38
  Apollo xp95 heat detector issue dcarney 8 2,316 05-12-2018, 10:34 PM
Last Post: Kibeth
  Morley Connexion Network issue Ghostrider 4 1,961 24-09-2018, 10:22 AM
Last Post: alonso

Forum Jump:


Users browsing this thread: 1 Guest(s)