Afternoon chaps

My Global Fire Website login is not letting me in and as a result I cant download the programming manual for the GFE 3 I/O PLUS Addressable Triple Input/Output Module.

Does anyone have a copy or anyone able to troubleshoot a configuration file that i've downloaded from the panel that is showing a fault with two newly installed modules?

Thanks in advance guys!
Reply
#2

.pdf   Addressable Module 3-Way I-O Unit.pdf (Size: 105.07 KB / Downloads: 69)

Is this what you are looking for
Peter Robinson




07889 038650

Reply
#3
Cheers mate but I have that one already.
I think there is a programming guide as well but cant login.

There are two I/O that are assigned in I/O group 512 in the input tab but there is no option to select group 512 (only up to 511) in the devices list and I want to see if there are any other boxes that should be ticked

Cheers


[Image: 1.png]
[Image: 2.png]
[Image: 3.png]
Reply
#4
Scroll backwards instead of forward.
Martin Wison
KGM Fire and Security Distribution Ltd.
Rochester, Kent.
01634 716882
http://www.kgmfireandsecurity.co.uk
Reply
#5
512 is the default common output group. All inputs will trigger this group regardless of the IO group setting.
Reply
#6
(04-11-2019, 10:46 AM)DPGB Wrote: 512 is the default common output group. All inputs will trigger this group regardless of the IO group setting.

Any I/O on the system must be programmed, they do not default to anything.
Martin Wison
KGM Fire and Security Distribution Ltd.
Rochester, Kent.
01634 716882
http://www.kgmfireandsecurity.co.uk
Reply
#7
What I meant was all inputs will trigger output group 512 regardless of the effect Grouping programming.
Reply
#8
(04-11-2019, 07:10 PM)DPGB Wrote: What I meant was all inputs will trigger output group 512 regardless of the effect Grouping programming.

Sorry, misunderstood. Yes 512 is the common group and will be activated on any fire.
Martin Wison
KGM Fire and Security Distribution Ltd.
Rochester, Kent.
01634 716882
http://www.kgmfireandsecurity.co.uk
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Manual Senator 11 4,328 06-12-2017, 11:28 PM
Last Post: bob1
  Manual Call point sign Tilly 4 3,443 23-03-2015, 11:37 PM
Last Post: Tilly
  protec 6300 programming ljarrald 19 20,910 29-10-2011, 08:24 AM
Last Post: hothead
  Morley zx1e programming lead Dan24 12 14,025 27-09-2011, 11:11 PM
Last Post: DPGB
  Rafiki manual Testing insructions mo2 0 1,635 26-07-2011, 11:10 PM
Last Post: mo2
Wink Thorn 1700 Installation Manual Andrew Jennings 8 6,885 17-08-2010, 04:04 PM
Last Post: martyarmstrong

Forum Jump:


Users browsing this thread: 1 Guest(s)