Hi Resistance on loop
#1
Hi all , having a problem with an advanced mx 4000 panel, 10 nodes on system with 4 loops on each panel. Have been servicing system for 6 months now (did not install it) no major issues to this point. This week 1 loop is showing a high resistance fault , I know this can be switched off in the mxpro5 en settings, but dont think you can on the 4000 series. Any ideas where to start with this issue, system is in really good order and well installed , approx 70 devices on this loop that causing fault. Thanks
Reply
#2
I normally start with open area sounders prone to moisture ingress, then move to sounder bases that have the earths connected on top of sounder as opposed to behing in the besa box
http://awacsuk.com

advanced warning and communicated systems
installation...integration...innovation....

any comments or views posted are mine and I'm keeping them.
Reply
#3
Break the loop down split it half way and see which side the fault is on as there is only 70 devices should be easy to locate
Peter Robinson




07889 038650

Reply
#4
Fastest way to rectify this fault is splitting loop in half,then faulty part again in half...At the end when you get some part of couple devices check them all. Maybe someone has damaged cable,or you will find some of the faults that guys pointed before.
Reply
#5
Iv had this issue recently, but the cause might not be the same as yours..

On mine it was crappy old Power sonic batteries causing the Loop 1 High Resistance fault to pop up. The loops were fine, I noticed the batteries were slightly warm so I assume they were putting the PSU under load. I noticed a difference in the loop output voltage by 0.8v+ after replacing them, the fault never came back.
Nothing is foolproof to a sufficiently talented fool...   24

Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Kentec Synchro hochiki Loop Explorer Software jmsa7 3 2,885 05-10-2019, 09:17 PM
Last Post: Ali Sulaiman
  SURGE PROTECTION ON LOOP Pro Metheus 2 707 10-04-2019, 09:25 PM
Last Post: Pro Metheus
  Kentec syncro as loop fault dcarney 13 2,748 23-02-2019, 10:58 PM
Last Post: Dan
  Gent Loop matthewhughes1 2 1,265 23-01-2019, 05:52 PM
Last Post: atherton1930
  New Apollo loop tester Next4467 9 1,710 12-12-2018, 12:03 AM
Last Post: Tilly
  Zeta Premier 4-Loop panel config and software ggiannopoulos 0 1,126 26-09-2018, 02:20 PM
Last Post: ggiannopoulos
  apollo 2nd loop sounders silent franksdr 11 3,156 24-09-2018, 09:52 PM
Last Post: hothead
  High resistance loop advanced mx pro 5 dcarney 18 7,039 05-05-2018, 09:09 PM
Last Post: Monkeh
  Hochiki Loop Tester kevinhynes 2 1,542 14-03-2018, 12:15 PM
Last Post: kevinhynes
  Advanced loop card short circuit testing xenex100 60 34,401 06-03-2018, 10:07 PM
Last Post: Monkeh

Forum Jump:


Users browsing this thread: 1 Guest(s)