disabled gate access control regs
#1
anyone know of any standards for disabled gates? at present the fire alarm signals to the gate as required and disabled gate opens correctly. however the gate controller seems to be a BPT unit with no backup supply - do these disabled exit gates need a backup psu for mains failure? is it sufficient for them to be turned off when the power goes off which presumably means they need to be physically moved open?

the disabled gate is in the middle between 2 access turnstiles from a factory main entrance so i suppose you could move either left or right along the fence if the gate was locked without having to re-enter the burning factory in a fire...

i've no idea if any bs coves disabled access gates.
Reply
#2
If it's in relation to the ability to use for escape then BS7273-4:2015 would seem most appropriate
Anthony Buck
Fire Safety Technical Lead @ BAFE SP205 accredited company
Extinguisher specialist

http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
http://www.linkedin.com/pub/anthony-buck/22/957/36b
Reply
#3
Yes, as Anthony pointed out. It will apply the same as automatic opening doors. A battery backup will be required
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#4
Ta all. I didn't know 7273 covered disabled gates. I'll have to read it!
No
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  CO alarm system regs. alonso 2 679 13-03-2020, 09:18 PM
Last Post: AnthonyB
  Maintenance regs leighton1471 4 1,432 24-10-2019, 10:40 AM
Last Post: Ghostrider
  Gas suppression panel regs alonso 25 10,912 22-01-2018, 07:35 PM
Last Post: hothead
  smokes either side of a fire released access door alonso 5 4,232 05-05-2017, 03:21 PM
Last Post: alonso
  access door relays Theoldman 9 6,233 22-09-2016, 08:48 AM
Last Post: Will Lloyd
  Regs around system re vamp Rubble1952 2 2,285 09-07-2015, 11:12 PM
Last Post: designguru
  Disabled refuge standards Ghostrider 7 5,169 07-07-2014, 07:33 AM
Last Post: Bill-J
  Relays for access control clarkson 38 29,378 17-12-2013, 07:47 PM
Last Post: Garsec
  Regs for two-linked panels? Beagle 13 19,999 07-06-2011, 11:12 PM
Last Post: hothead
  New regs for door relays skelffie 24 28,421 21-01-2011, 06:54 PM
Last Post: Ian Warrick

Forum Jump:


Users browsing this thread: 1 Guest(s)