Advanced - Config ram fail
#1
Anyone know what causes it? Iv got an MX4200 that's less than 2 years old. I serviced it about a week ago, this morning it went into fault with a Config Ram Fail. I rebooted the panel and the fault has not come back touch wood. Cheers.
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#2
Happens now and again and the warm start is the solution - not sure why tbh
All posts are of my own opinion and knowledge and do not reflect the views of the Company I work for.
Reply
#3
Hi Dan,

This is typically caused by someone making configuration changes via the Level 3 menus whilst the memory lock jumper is in the "Locked" position, then exiting Level 3. The panel attempts to write the new data to the RAM but is unable to, a config fail message is then generated to bring the issue to your attention, a reboot will clear this but any alterations would be lost and in need of re-doing, a typical example would be the recent influx of Service Due faults.

BR,

Tech Support.
Reply
#4
(28-01-2020, 04:55 PM)Advel Tech Support Wrote: Hi Dan,

This is typically caused by someone making configuration changes via the Level 3 menus whilst the memory lock jumper is in the "Locked" position, then exiting Level 3. The panel attempts to write the new data to the RAM but is unable to, a config fail message is then generated to bring the issue to your attention, a reboot will clear this but any alterations would be lost and in need of re-doing, a typical example would be the recent influx of Service Due faults.

BR,

Tech Support.

Have to remember that one :)
Peter Robinson




07889 038650

Reply
#5
(28-01-2020, 04:55 PM)Advel Tech Support Wrote: Hi Dan,

This is typically caused by someone making configuration changes via the Level 3 menus whilst the memory lock jumper is in the "Locked" position, then exiting Level 3. The panel attempts to write the new data to the RAM but is unable to, a config fail message is then generated to bring the issue to your attention, a reboot will clear this but any alterations would be lost and in need of re-doing, a typical example would be the recent influx of Service Due faults.

BR,

Tech Support.

I was going to say same thing if the Engineer had just been working on the system but didn't realise of could happen a while after.

Influx of service date faults ?  I cant say I noticed any here :)
All posts are of my own opinion and knowledge and do not reflect the views of the Company I work for.
Reply
#6
(28-01-2020, 04:55 PM)Advel Tech Support Wrote: Hi Dan,

This is typically caused by someone making configuration changes via the Level 3 menus whilst the memory lock jumper is in the "Locked" position, then exiting Level 3. The panel attempts to write the new data to the RAM but is unable to, a config fail message is then generated to bring the issue to your attention, a reboot will clear this but any alterations would be lost and in need of re-doing, a typical example would be the recent influx of Service Due faults.

BR,

Tech Support.

Ta very much. Il check the memory lock jumper isn't on when I next go. Didn't think to check that.
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#7
Was that mentioned on the bulletin sent out by Advel ?
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Advanced 360 account restricted? Dan 4 403 20-11-2019, 11:54 PM
Last Post: Tilly
  Frustrating Loop Open Circuit on Advanced MX5 Pro Dan 8 607 18-11-2019, 12:33 PM
Last Post: Graeme
  Institute of Advanced Drivers free e-learning modules Ghostrider 0 458 23-03-2019, 02:10 PM
Last Post: Ghostrider
  Advanced investigation delay Senator 9 2,367 27-06-2018, 06:46 PM
Last Post: sparky999
  Advanced 360 atherton1930 6 3,097 04-10-2017, 08:23 AM
Last Post: atherton1930
  Advanced qrp file John 3 2,426 12-06-2017, 10:25 PM
Last Post: John
  advanced panel XP95 detection fozzy 17 14,860 12-05-2015, 07:54 PM
Last Post: Will1989
  Advanced Graphics alex88 12 8,436 13-04-2015, 09:37 PM
Last Post: alex88
  another pub fail oasistechnical 5 3,340 11-07-2013, 08:04 AM
Last Post: oasistechnical
Exclamation Trouble Shooting a firelite comm fail - help? Total Package 2 6,962 08-09-2012, 10:42 PM
Last Post: Kibeth

Forum Jump:


Users browsing this thread: 1 Guest(s)