Advanced loop card failure Mx5 Pro
#1
Iv had two call out this year to two completely separate sites, both have Mx5 Pro and are fairly new. Both suffered a blown loop card. I checked the loop wiring for short circuits, earth faults etc but I could never find a cause. I replaced the failed loop cards on both jobs and both panels have sat happy since. I just find it a bit bizarre that I was never able to find a cause. On both loop cards it's what looks to be the relay for the loop isolator that's melted. Anyone had something similar? 

   
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#2
I must say that for the amount of panels we sell we have very few sales of individual loop cards, so I wouldn't say it was too common.
Martin Wison
KGM Fire and Security Distribution Ltd.
Rochester, Kent.
01634 716882
http://www.kgmfireandsecurity.co.uk
Reply
#3
What current is each loop pulling?
Reply
#4
The loop could be picking up a spike from somewhere
Peter Robinson




07889 038650

Reply
#5
Looks like the capacitor that has gone pop, C3.
Reply
#6
(05-06-2020, 01:08 PM)MD Martin Wrote: I must say that for the amount of panels we sell we have very few sales of individual loop cards, so I wouldn't say it was too common.

Cheers mate
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#7
(05-06-2020, 06:36 PM)Royce44 Wrote: What current is each loop pulling?

Moderate, nothing higher than usual.
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#8
(05-06-2020, 09:12 PM)sparky999 Wrote: The loop could be picking up a spike from somewhere

Yep that's what I'm starting to think
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#9
(05-06-2020, 10:03 PM)Adi Wrote: Looks like the capacitor that has gone pop, C3.

I thought it was a relay! I must get to specsavers once they reopen.......
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#10
(06-06-2020, 08:15 AM)Dan Wrote:
(05-06-2020, 10:03 PM)Adi Wrote: Looks like the capacitor that has gone pop, C3.

I thought it was a relay! I must get to specsavers once they reopen.......

Tell them your an MP, Simples
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Advanced mx4000 networking dcarney 8 732 24-06-2020, 03:08 PM
Last Post: davefiresafety
  Hi Resistance on loop dcarney 4 936 11-12-2019, 01:01 AM
Last Post: Dan
  Advanced mxpro 4 intermittent open circuit jordanjor 8 1,427 09-10-2019, 04:43 PM
Last Post: MD Martin
  Kentec Synchro hochiki Loop Explorer Software jmsa7 3 3,357 05-10-2019, 09:17 PM
Last Post: Ali Sulaiman
  EM Vents - Advanced MxPro5 Next4467 7 1,612 29-08-2019, 02:30 PM
Last Post: Next4467
  Advanced disablement via keyswitch input alonso 2 813 30-07-2019, 06:50 PM
Last Post: Mr C
  Advanced call point delays Bero 2 947 11-06-2019, 02:25 PM
Last Post: sparky999
  Advanced C&E Senator 10 2,859 15-04-2019, 10:49 PM
Last Post: Senator
  SURGE PROTECTION ON LOOP Pro Metheus 2 895 10-04-2019, 09:25 PM
Last Post: Pro Metheus
  ems and advanced Advel Tech Support alonso 14 2,677 06-03-2019, 12:55 AM
Last Post: dubfireengineer

Forum Jump:


Users browsing this thread: 1 Guest(s)