Xp95 I/O unit input earth fault
#1
Have an Advanced MX pro panel with an xp95 I/O unit with an earth fault on the input showing on the panel, IO has been changed, cable changed and disconnected from far end of cable but still fault returns, anyone experience this
Reply
#2
(14-07-2020, 05:05 PM)Bero Wrote: Have an Advanced MX pro panel with an xp95 I/O unit with an earth fault on the input showing on the panel, IO has been changed, cable changed and disconnected from far end of cable but still fault returns, anyone experience this

Have you tried changing the I/O unit for another one
Peter Robinson




07889 038650

Reply
#3
Yes, already changed
Reply
#4
If you don't get the fault with the eol connected straight into the io, but you do with the eol connected at the far end of the cable, then it's the cable.
If you only get it when the external equipment is connected, then there's something on the equipment causing it.

I had one once with a gas suppression panel I was monitoring when they connected it in to a voltage output instead of a dry contact.
Reply
#5
As above seen it caused by 3rd party equipment when the input is active.
Reply
#6
Also had this on the vesda VEP's, contact was kicking out 5v.
Whistle Admit to nothing, deny everythingWhistle
Reply
#7
Make sure dill switch 128 is off.
Reply
#8
(15-07-2020, 05:53 AM)COMM ENGINEER Wrote: Make sure dill switch 128 is off.

That doesn’t usually cause an earth fault. Will just double address whatever the other switches add up to
Reply
#9
The CPC of 3rd Party equipment connected to same terminations for loop screen?
All posts are of my own opinion and knowledge and do not reflect the views of the Company I work for.
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  earth fault only occurs whilst testing devices? alonso 14 1,222 22-03-2020, 12:21 PM
Last Post: Dan
  gent network fault alonso 1 950 30-10-2019, 09:59 PM
Last Post: Harrysu
  CTEC CFP and XP95 Interface dazmisiak 3 1,000 28-08-2019, 05:41 PM
Last Post: Dan
  Advanced disablement via keyswitch input alonso 2 934 30-07-2019, 06:50 PM
Last Post: Mr C
  Kentec syncro as loop fault dcarney 13 3,840 23-02-2019, 10:58 PM
Last Post: Dan
  Morley DX initization fault lotso bear 5 1,756 11-02-2019, 07:34 PM
Last Post: sparky999
  Apollo xp95 sounder base faulty dcarney 20 4,890 02-01-2019, 12:43 PM
Last Post: wozzer38
  Apollo XP95 Addressing doublefrick 35 8,775 14-12-2018, 09:16 AM
Last Post: Tilly
  Output short circuit fault dcarney 8 2,428 12-12-2018, 04:50 PM
Last Post: Allen Higginson
  Apollo xp95 heat detector issue dcarney 8 2,076 05-12-2018, 10:34 PM
Last Post: Kibeth

Forum Jump:


Users browsing this thread: 1 Guest(s)