#1
Hi Guys

Lovely weather we are having! Hit 38 degrees on the car dashboard in Leeds.

I have a site with a ZP3, the panel died this afternoon, tried everything I could think of to get it back up and running but it looks like it is completely goosed. Not found a cause for it either. I have made a few calls and managed to purchase a brand new ZP3, should be arriving on Monday. As you may know I don't have a great deal of experience with Ziton, I only have a couple of sites with them and this is the first time I have had an issue with one. My question is I do have an up to date site file, luckily I only amended some text in this panel in May. If I swap out the panel like for like, will it be just as straight forward as uploading my recent site file into the replacement panel?

Thanks, have a good weekend guys.
Dan
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#2
You'll need to adjust the firmware version and panel type. so say yours was a version 1 panel, just amend it to a 3.12 (assuming yours is brand new) and make sure the panel type is amended too. Also you will need to change the comms to the correct setting in peripheral settings (11 I think without a panel in front of me) And the node address if on a network. Other than that yeah pretty easy.
Whistle Admit to nothing, deny everythingWhistle
Reply
#3
Perfect. Just what I wanted to hear.

Cheers matey
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#4
Before you start, download the panel, and take a copy of the folder and save it somewhere else, docs etc, so you have a spare. If the software crashes you can loose the site file.
Version 2 to 3, as above, quite easy. May have to check a version 1 to 3 upload as somethings are slightly different, and have a run through the cause and effects to make sure the same.
http://awacsuk.com

advanced warning and communicated systems
installation...integration...innovation....

any comments or views posted are mine and I'm keeping them.
Reply
#5
And as Kilbeth says, protocol version 11, set baud rate in peripherals.
http://awacsuk.com

advanced warning and communicated systems
installation...integration...innovation....

any comments or views posted are mine and I'm keeping them.
Reply
#6
Thanks Doug. I'm hoping the old panel is a V2, think it was fitted at around 2008 when the building was built. Will let you know if I run into any problems.
Nothing is foolproof to a sufficiently talented fool...   24

Reply
#7
No worries Dan, give me a call from site if you have any issues.
http://awacsuk.com

advanced warning and communicated systems
installation...integration...innovation....

any comments or views posted are mine and I'm keeping them.
Reply
#8
Think current version is 3.12 as swapped one the other day, although sure I did a 3.14 last year.
If there is a double knock cause and effect set up, be a little careful.
If you set the panel to zonal double knock it does not bring the panel into fire on the fire activation, only an"alarm" condition.
Found this a bit troubling but tech say that's the way their software guys are interpretating the last EN54 stuff.
http://awacsuk.com

advanced warning and communicated systems
installation...integration...innovation....

any comments or views posted are mine and I'm keeping them.
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Hochiki and Advanced mxpro5 panel dcarney 3 238 29-07-2020, 09:05 PM
Last Post: dcarney
  Help to identify panel davefiresafety 7 552 24-06-2020, 02:48 PM
Last Post: davefiresafety
  Aritech UTC fire panel issues dcarney 4 689 27-04-2020, 06:36 PM
Last Post: Graeme
  Ziton ZP3 cal points Next4467 5 2,414 24-06-2019, 05:04 PM
Last Post: Underdog
  Lightning damage fire alarm panel dcarney 9 2,077 15-03-2019, 12:38 PM
Last Post: kevinhynes
  Ziton zp3 walk test dcarney 9 2,759 16-02-2019, 01:57 PM
Last Post: Monkeh
Question Anyone recognise this panel? Dan 5 1,882 16-01-2019, 01:40 PM
Last Post: Chris M.
  C-Tec XFP fire panel Device names not correct dali 33 13,052 11-12-2018, 05:10 AM
Last Post: sadiquereliant
  Class change Senator 3 1,103 06-12-2018, 07:48 PM
Last Post: sparky999
  Gent Nano change device type Bero 2 1,162 27-11-2018, 11:17 AM
Last Post: Bero

Forum Jump:


Users browsing this thread: 1 Guest(s)