Sprinkler Flow Switch Zone?

Hello Everyone,
We have recently being asked to connect a sprinkler flow switch to the house Fire Alarm system, which i have no problems with at all, my question is does a sprinkler flow switch have to be allocated its own zone? or can you add it to a currently installed zone? I only ask because in experience of servicing this type of system, the flow switch usually has its own zone. Any Help with this would be greatly appreciated.

28-07-2010 08:06 PM
Find all posts by this user Quote this message in a reply
CerbNI
Super Moderator
******


Posts: 971
Group: Super Moderators
Joined: Apr 2009
Status: Online
Reputation: 5
Post: #2
RE: Sprinkler Flow Switch Zone?

Rob-Leeds Wrote:
Hello Everyone,
We have recently being asked to connect a sprinkler flow switch to the house Fire Alarm system, which i have no problems with at all, my question is does a sprinkler flow switch have to be allocated its own zone? or can you add it to a currently installed zone? I only ask because in experience of servicing this type of system, the flow switch usually has its own zone. Any Help with this would be greatly appreciated.


Like you,I have always allocated flow switches a zone of their own but never stopped to ask why - it just always has been the case.
Practically,it is near impossible to decide if a flow switch has activated without taking it apart and metering it (unless you have fitted a local visual indicator of it) so it would make confirming where the activation was within a zone difficult.

28-07-2010 08:50 PM
Find all posts by this user Quote this message in a reply
gla.ssfs
Administrator
*******


Posts: 249
Group: Administrators
Joined: Mar 2008
Status: Online
Reputation: 2
Post: #3
RE: Sprinkler Flow Switch Zone?

Same here, Always own its own zone for identification reasons


South Staffs Fire & Security Ltd
Tel: 01543 496382
info@southstaffsfire.co.uk
http://www.southstaffsfire.co.uk
28-07-2010 10:16 PM
Visit this user's website Find all posts by this user Quote this message in a reply
douglas docherty
Administrator
*******


Posts: 1,055
Group: Administrators
Joined: Mar 2008
Status: Online
Reputation: 9
Post: #4
RE: Sprinkler Flow Switch Zone?

El ditto. Always put it in it's own marked up seperate zone. Let's you know the flow switch has activated, not necessarily always a fire condition, but should be responded to as such.


http://awacsuk.com

advanced warning and communicated systems
installation...integration...innovation....

any comments or views posted are mine and I'm keeping them.
28-07-2010 10:20 PM
Visit this user's website Find all posts by this user Quote this message in a reply
barryc
Fire Engineer
****


Posts: 82
Group: Fire Engineer
Joined: Oct 2008
Status: Online
Reputation: 0
Post: #5
RE: Sprinkler Flow Switch Zone?

I find it easier for the customer if its in a separate zone. They can disable just the sprinkler zone when its been serviced

28-07-2010 10:29 PM
Find all posts by this user Quote this message in a reply
kevin hynes
Fire Engineer
****


Posts: 107
Group: Fire Engineer
Joined: Jan 2009
Status: Online
Reputation: 0
Post: #6
RE: Sprinkler Flow Switch Zone?

barryc Wrote:
I find it easier for the customer if its in a separate zone. They can disable just the sprinkler zone when its been serviced


Same as , always connect to its own allocated zone, although if its a house alarm system with only a few devices and it would be diificult or require another panel i would stick it on an existing zone

29-07-2010 01:55 PM
Find all posts by this user Quote this message in a reply
Rob-Leeds
Fire Engineer
****


Posts: 3
Group: Fire Engineer
Joined: Jul 2010
Status: Offline
Reputation: 0
Post: #7
RE: Sprinkler Flow Switch Zone?

Cheers Guys, Yeah the building is due for a refit in the next two years, and its a 4 zone conventional panel with a zone allocated to each floor, so it would have to be a new panel. I was just wondering if in the regs it specifically has to be on its own zone, or whether it just classes as a device? Thanks for all your opinions.

30-07-2010 01:04 AM
Find all posts by this user Quote this message in a reply
colin w
Test & Comms
******


Posts: 343
Group: Super Moderators
Joined: Jun 2009
Status: Offline
Reputation: 0
Post: #8
RE: Sprinkler Flow Switch Zone?

If your going to fit this on a conventional panel it should be able to be isolated by the client IE key switch etc this opens a can of worms I had a site with a sprinkler zone the system was drained for testing and then could not be refilled due to a fault which took six weeks to fix no one wanted to pay for the switch to be dissed from the system until the sprinklers were fixed the client said it was down to the sprinkler company and vice-verse they kept on calling the fault in under there service contract as the panel was in fault but as the key was isolated so round and round it went in the end I went to the shopping center management on the off chance they could help to find the sprinkler flow switch was in fact theirs and under contract with another company and they new nothing of the problem with the local sprinklers this did cause a s..t storm for the shop in the end the switch was wired to the house system 2 days before the pipe was repaired.

30-07-2010 09:43 PM
Find all posts by this user Quote this message in a reply
Post Reply  Post Thread 

[-]
Quick Reply
Message
Type your reply to this message here.



Image Verification
Image Verification Please enter the text within the image on the left in to the text box below. This process is used to prevent automated posts.

View a Printable Version
Send this Thread to a Friend
Subscribe to this Thread | Add Thread to Favorites
Rate This Thread:

Forum Jump: