Emergency Lighting Cable?
19-03-2011, 11:12 AM
Post: #1
Emergency Lighting Cable?
I've just read on another post that emergency lights should be wired in fire proof cable.

I can see the point when there is a central battery backup involved.

But whats the point in wiring a self contained fitting in FP? Surley its benificial to have the fitting supply cable burn through?

Have I missed something here? Rules

LOZ!

GB Surveillance
Suppliers of covert surveillance equipment and other products and services.

Find all posts by this user
Quote this message in a reply
19-03-2011, 11:39 AM
Post: #2
RE: Emergency Lighting Cable?
I was under the impression that self-contained could be in normal cable but the central battery systems had to be in FP.
Find all posts by this user
Quote this message in a reply
19-03-2011, 12:09 PM
Post: #3
RE: Emergency Lighting Cable?
lozevans555 Wrote:I've just read on another post that emergency lights should be wired in fire proof cable.

I can see the point when there is a central battery backup involved.

But whats the point in wiring a self contained fitting in FP? Surley its benificial to have the fitting supply cable burn through?

Have I missed something here? Rules

LOZ!

I am certain that self contained units can be wired in non FP cable, unless the regs have changed recently , but cant see any benefit in FP cable
Find all posts by this user
Quote this message in a reply
19-03-2011, 12:33 PM
Post: #4
RE: Emergency Lighting Cable?
firemonkey Wrote:I was under the impression that self-contained could be in normal cable but the central battery systems had to be in FP.

kevin hynes Wrote:I am certain that self contained units can be wired in non FP cable, unless the regs have changed recently , but cant see any benefit in FP cable

I'm not going mad then Cool

GB Surveillance
Suppliers of covert surveillance equipment and other products and services.

Find all posts by this user
Quote this message in a reply
19-03-2011, 01:21 PM
Post: #5
RE: Emergency Lighting Cable?
lozevans555 Wrote:
firemonkey Wrote:I was under the impression that self-contained could be in normal cable but the central battery systems had to be in FP.

kevin hynes Wrote:I am certain that self contained units can be wired in non FP cable, unless the regs have changed recently , but cant see any benefit in FP cable

I'm not going mad then Cool

Yeah fp is only required on CBU's
Find all posts by this user
Quote this message in a reply
19-03-2011, 04:40 PM
Post: #6
RE: Emergency Lighting Cable?
lozevans555 Wrote:I've just read on another post that emergency lights should be wired in fire proof cable.

the only reason would be to surface mount the cable?

however you can get white non fp "earth protection" or whatever nowadays ?
Find all posts by this user
Quote this message in a reply
19-03-2011, 09:46 PM
Post: #7
RE: Emergency Lighting Cable?
unless it CBU then you cant use FP, it has to be the same as the cable that is used in wiring the lighting circuit.

Then, if you have 3 hour duration to maintain, how TF do you comply, standard fp is out the window, and enhanced is only an hour or so if memory serves us correctly.

Adi Bosworth
ADI Security Solutions
Fire and intruder detection
http://www.adisecuritysolutions.co.uk
Find all posts by this user
Quote this message in a reply
20-03-2011, 11:24 AM
Post: #8
RE: Emergency Lighting Cable?
Can't find my 5266 but I know it specifically states that self contained EL should be wired in similar cable to the normal wiring.

Simply because if there is a fire and the normal lighting cable burns through you don't want a fire proof cable maintaining the electrical feed to the EL fitting thereby preventing it from turning on.

===================================
Some men aren't looking for anything logical. They can't be bought, bullied, reasoned, or negotiated with. Some men just want to watch the world burn.

Established Since 1985 - BAFE SP203 - Wireless Fire Alarm System Specialists - Gent 24
http://www.ctafire.co.uk
Visit this user's website Find all posts by this user
Quote this message in a reply
20-03-2011, 01:13 PM
Post: #9
RE: Emergency Lighting Cable?
Bingoooooooooooooooooooooooooooooooooooooo

(hopefully bingo is now bigger to post) :)

Adi Bosworth
ADI Security Solutions
Fire and intruder detection
http://www.adisecuritysolutions.co.uk
Find all posts by this user
Quote this message in a reply
20-03-2011, 06:40 PM
Post: #10
RE: Emergency Lighting Cable?
Hi might have been me that started this discussion, I have been assured that it is all new cabling to any emergency light. I will go back to my font of all knowledge tomorrow to get chapter & verse (unless Lance reads this and confirms my statements)
Find all posts by this user
Quote this message in a reply
Post Reply 


Possibly Related Threads...
Thread: Author Replies: Views: Last Post
  LED EM lighting Tilly 3 249 03-05-2014 07:44 AM
Last Post: Tilly
  Emergency Light Batteries murphy21 7 355 13-04-2014 07:35 AM
Last Post: Leolion2177
  Anyone make up their own Emergency Light Battery Packs? Leolion2177 13 2,845 16-11-2012 04:58 PM
Last Post: Leolion2177
  Warehouse emergency lighting help please... Ghostrider 18 5,907 25-10-2012 08:24 PM
Last Post: Ferret
  Self Test Emergency Lights alex1982 8 2,947 12-08-2012 07:07 PM
Last Post: alex1982
  Emergency Lighting Survey-Please contribute douglas docherty 8 2,691 18-05-2012 07:23 PM
Last Post: Adi
  Emergency Lighting - Suppliers miles 18 4,881 31-03-2012 07:59 PM
Last Post: Garsec
  Emergency lighting Research miles 0 1,134 28-03-2012 10:06 AM
Last Post: miles
  New Code of Practice for Installation of Emergency Lighting admin 2 2,012 22-02-2012 01:31 PM
Last Post: AnthonyB
  BS 5266-1:2011 Code of practice for the emergency escape lighting of premises AnthonyB 0 3,424 18-11-2011 06:46 PM
Last Post: AnthonyB

Forum Jump:


User(s) browsing this thread: 1 Guest(s)

Contact Us | Fire Alarm Engineers | Return to Top | Return to Content | Lite (Archive) Mode | RSS Syndication