Chloride Gent 85 Mk11 fire alarm unit
#1
Sad 
Hello
I have an old Chloride Gent 85 Mk11 fire alarm unit that has developed a fault and I need to relace the panel, it is a 2 wire system for smoke and call points and seperate 2 wires for the bells. I need to add more smoke detectors to the system is there a panel that would replace like for like or is it a question of replacing the whole system?

Regards Keith
Reply
#2
asking this means u know nothing about fire systems, so i don't think you should be changing it.

any conventional 2 zone fire panel will do, connect bells into bell/sounder output put eol at last bell if 24v. same with mcp's connect to zone 1, eol at last device, if the mcp are old might not have 470ohm resistor in them, that case need to fit one at each device in series on any leg.
Reply
#3
carefull!!! some of the early gent 85s were 3 wire!! and are normally spurred everywere...
Reply
#4
yeah but he said that was a normal 2 wire
Reply
#5
Another point is that most of these panels also used AC detectors along with the zone EOL being a diode, that will not work on any other panels.

There were also limitations on the quantity of detectors that could be installed although the units could be interconnected to give larger coverage.

The only recommendation would be to replace ALL the component parts of the system including call points with new.
Reply
#6
what kind of fault has it developed? is it definitely inside the panel and not out on the field wiring?
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Gent Vigilon dekoya 13 523 30-03-2017, 02:39 PM
Last Post: douglas docherty
  gent v sms alonso 4 311 22-03-2017, 08:48 PM
Last Post: luggsey
  Wiring open collector of fire panel gherasim 19 849 13-02-2017, 07:46 PM
Last Post: Monkeh
  Gent S quad head John 5 389 09-02-2017, 03:25 PM
Last Post: atherton1930
  Fire panel output types gherasim 7 576 01-02-2017, 09:18 AM
Last Post: gherasim
  Fire Alarm Control Panel -- Reliability of Function - Guess Fire-Sal 16 1,439 30-01-2017, 09:44 PM
Last Post: designguru
  Name the beam unit unimatrix1066 4 392 01-01-2017, 12:26 AM
Last Post: barryc
  2 gent vigilon issues alonso 4 738 14-09-2016, 09:30 PM
Last Post: Monkeh
  ZITON FIRE ALARM CONTROL PANEL ahmedmahgoub 3 1,126 04-08-2016, 09:49 PM
Last Post: designguru
  Interserve Fire kevin hynes 9 887 13-06-2016, 09:33 AM
Last Post: bob1

Forum Jump:


Users browsing this thread: 1 Guest(s)