Chloride Gent 85 Mk11 fire alarm unit
27-03-2009, 05:31 PM
Post: #1
Sad Chloride Gent 85 Mk11 fire alarm unit
Hello
I have an old Chloride Gent 85 Mk11 fire alarm unit that has developed a fault and I need to relace the panel, it is a 2 wire system for smoke and call points and seperate 2 wires for the bells. I need to add more smoke detectors to the system is there a panel that would replace like for like or is it a question of replacing the whole system?

Regards Keith
Find all posts by this user
Quote this message in a reply
01-05-2009, 05:51 PM
Post: #2
RE: Chloride Gent 85 Mk11 fire alarm unit
asking this means u know nothing about fire systems, so i don't think you should be changing it.

any conventional 2 zone fire panel will do, connect bells into bell/sounder output put eol at last bell if 24v. same with mcp's connect to zone 1, eol at last device, if the mcp are old might not have 470ohm resistor in them, that case need to fit one at each device in series on any leg.
Quote this message in a reply
03-05-2009, 06:38 PM
Post: #3
RE: Chloride Gent 85 Mk11 fire alarm unit
carefull!!! some of the early gent 85s were 3 wire!! and are normally spurred everywere...
Find all posts by this user
Quote this message in a reply
04-05-2009, 02:20 PM
Post: #4
RE: Chloride Gent 85 Mk11 fire alarm unit
yeah but he said that was a normal 2 wire
Quote this message in a reply
10-06-2009, 03:33 PM
Post: #5
RE: Chloride Gent 85 Mk11 fire alarm unit
Another point is that most of these panels also used AC detectors along with the zone EOL being a diode, that will not work on any other panels.

There were also limitations on the quantity of detectors that could be installed although the units could be interconnected to give larger coverage.

The only recommendation would be to replace ALL the component parts of the system including call points with new.
Find all posts by this user
Quote this message in a reply
10-06-2009, 08:08 PM
Post: #6
RE: Chloride Gent 85 Mk11 fire alarm unit
what kind of fault has it developed? is it definitely inside the panel and not out on the field wiring?
Find all posts by this user
Quote this message in a reply
Post Reply 


Possibly Related Threads...
Thread: Author Replies: Views: Last Post
  GENT UKNerd 12 601 18-05-2013 02:50 PM
Last Post: ESP
  multi alarm uni ifax software problem dan ross 18 3,624 15-05-2013 04:17 PM
Last Post: UKNerd
  Suitable replacement fire panel andyfire 18 790 23-04-2013 09:18 PM
Last Post: ESP
  old gent detector doublefrick 8 462 15-04-2013 03:11 PM
Last Post: Ian Warrick
  voyager fire panel UKNerd 28 931 07-04-2013 06:23 PM
Last Post: ali alameh
  Gent Vigilon Compact Loop Card Fault mjr2000 5 466 18-03-2013 11:32 PM
Last Post: douglas docherty
  conventional pre alarm? ljarrald 3 354 07-03-2013 10:53 AM
Last Post: wozzer38
  Complaints About Alarm Testing Company murphy21 28 1,267 24-02-2013 11:07 AM
Last Post: Ghostrider
  gent xens 801 mcp owolabi 0 217 11-02-2013 05:41 PM
Last Post: owolabi
  Fire shutter control panel alonso 5 572 10-02-2013 11:48 PM
Last Post: alonso

Forum Jump:


User(s) browsing this thread: 2 Guest(s)

Contact Us | Fire Alarm Engineers | Return to Top | Return to Content | Lite (Archive) Mode | RSS Syndication