Chloride Gent 85 Mk11 fire alarm unit
#1
Sad 
Hello
I have an old Chloride Gent 85 Mk11 fire alarm unit that has developed a fault and I need to relace the panel, it is a 2 wire system for smoke and call points and seperate 2 wires for the bells. I need to add more smoke detectors to the system is there a panel that would replace like for like or is it a question of replacing the whole system?

Regards Keith
Reply
#2
asking this means u know nothing about fire systems, so i don't think you should be changing it.

any conventional 2 zone fire panel will do, connect bells into bell/sounder output put eol at last bell if 24v. same with mcp's connect to zone 1, eol at last device, if the mcp are old might not have 470ohm resistor in them, that case need to fit one at each device in series on any leg.
Reply
#3
carefull!!! some of the early gent 85s were 3 wire!! and are normally spurred everywere...
Reply
#4
yeah but he said that was a normal 2 wire
Reply
#5
Another point is that most of these panels also used AC detectors along with the zone EOL being a diode, that will not work on any other panels.

There were also limitations on the quantity of detectors that could be installed although the units could be interconnected to give larger coverage.

The only recommendation would be to replace ALL the component parts of the system including call points with new.
Reply
#6
what kind of fault has it developed? is it definitely inside the panel and not out on the field wiring?
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  BS7273-4 compliant interface to fire alarm panel CaptainSlog 33 726 Yesterday, 02:12 AM
Last Post: CaptainSlog
  gent vigilon network command builds alonso 3 177 28-12-2017, 10:10 PM
Last Post: Harrysu
  Gent I/O Unit RMC 5 359 25-11-2017, 01:46 AM
Last Post: douglas docherty
  Gent 3505 Terminal Node Alex Milner 9 686 26-10-2017, 06:55 PM
Last Post: Alex Milner
  30 Minutes Fire Protection - Meter Box murphy21 5 577 20-09-2017, 08:27 AM
Last Post: Tilly
  Gent Nano eeprom failed phil goodge 4 762 11-09-2017, 07:26 AM
Last Post: phil goodge
  false alarm conventional smoke in a h.v. room alonso 12 1,613 13-08-2017, 01:28 PM
Last Post: bob1
  Gent Vigilon dekoya 13 2,477 30-03-2017, 02:39 PM
Last Post: douglas docherty
  gent v sms alonso 4 951 22-03-2017, 08:48 PM
Last Post: luggsey
  Wiring open collector of fire panel gherasim 19 3,711 13-02-2017, 07:46 PM
Last Post: Monkeh

Forum Jump:


Users browsing this thread: 1 Guest(s)