Chloride Gent 85 Mk11 fire alarm unit
27-03-2009, 04:31 PM
Post: #1
Sad Chloride Gent 85 Mk11 fire alarm unit
Hello
I have an old Chloride Gent 85 Mk11 fire alarm unit that has developed a fault and I need to relace the panel, it is a 2 wire system for smoke and call points and seperate 2 wires for the bells. I need to add more smoke detectors to the system is there a panel that would replace like for like or is it a question of replacing the whole system?

Regards Keith
Find all posts by this user
Quote this message in a reply
01-05-2009, 04:51 PM
Post: #2
RE: Chloride Gent 85 Mk11 fire alarm unit
asking this means u know nothing about fire systems, so i don't think you should be changing it.

any conventional 2 zone fire panel will do, connect bells into bell/sounder output put eol at last bell if 24v. same with mcp's connect to zone 1, eol at last device, if the mcp are old might not have 470ohm resistor in them, that case need to fit one at each device in series on any leg.
Quote this message in a reply
03-05-2009, 05:38 PM
Post: #3
RE: Chloride Gent 85 Mk11 fire alarm unit
carefull!!! some of the early gent 85s were 3 wire!! and are normally spurred everywere...
Find all posts by this user
Quote this message in a reply
04-05-2009, 01:20 PM
Post: #4
RE: Chloride Gent 85 Mk11 fire alarm unit
yeah but he said that was a normal 2 wire
Quote this message in a reply
10-06-2009, 02:33 PM
Post: #5
RE: Chloride Gent 85 Mk11 fire alarm unit
Another point is that most of these panels also used AC detectors along with the zone EOL being a diode, that will not work on any other panels.

There were also limitations on the quantity of detectors that could be installed although the units could be interconnected to give larger coverage.

The only recommendation would be to replace ALL the component parts of the system including call points with new.
Find all posts by this user
Quote this message in a reply
10-06-2009, 07:08 PM
Post: #6
RE: Chloride Gent 85 Mk11 fire alarm unit
what kind of fault has it developed? is it definitely inside the panel and not out on the field wiring?
Find all posts by this user
Quote this message in a reply
Post Reply 


Possibly Related Threads...
Thread: Author Replies: Views: Last Post
  Gent nano Cristafar 3 169 10-04-2014 10:42 AM
Last Post: douglas docherty
  New Gent Panel to replace the vigi UKNerd 17 552 07-04-2014 04:56 PM
Last Post: ESP
  Fault in Autronica BS100 Fire Alarm Panel tejo.251 3 221 27-03-2014 01:03 PM
Last Post: atherton1930
  Gent 8000 kevin hynes 9 4,122 14-02-2014 04:26 PM
Last Post: zenengineering
  Vega Panel alarm krahim4 1 229 11-02-2014 01:56 PM
Last Post: Ian Warrick
  Minerva Marine T1008 Fire Panel Manual needed contractor999 15 14,292 05-02-2014 08:28 AM
Last Post: indiaszagalo
  Radio fire system bob1 22 1,912 02-01-2014 10:10 PM
Last Post: UKNerd
  Fire Engineer Training savodump 17 1,638 27-12-2013 12:14 AM
Last Post: Monkeh
  Different Buildings - Connected Fire Alarm Panels aeg 16 1,502 14-12-2013 03:02 PM
Last Post: jmeservices
  newlec/bardic 4 zone panel jumper & fire relay alonso 3 534 10-12-2013 08:22 PM
Last Post: w00ds

Forum Jump:


User(s) browsing this thread: 1 Guest(s)

Contact Us | Fire Alarm Engineers | Return to Top | Return to Content | Lite (Archive) Mode | RSS Syndication