open circuit fault
#1
Hi can anyone help,i have a open circuit on loop 2 on a Kentec 8000 addr fire alarm panel which has Apollo xp95 heads /sounder/beacons ect....I have taken out the return pair and noted then the other pair with no joy.Also i have taken out a paif and measured for voltage and listed all without replaced pair and took out the other pair and measured for voltage on the 1st 9 devices without voltage on the 2nd 31 without voltage still though no closer to finding fault certainly not a head/base as works are continual in this new build!There is no access in the roof space so cannot trace cables.Any ideas would be appreciated there are 40 devices on loop 2.
Reply
#2
You can take out each side of the loop and see which devices disappear on the panel. So you just have one side of the loop in the panel. You can then get an idea where the loop is open circuit and trace it from there.

Hmmmm. Are you an fire engineer or a electrician? Just asking.
Reply
#3
Hi i am an electrician,new to fire alarms as i said earlier i took out a pair from the panel and lost 9{devices dissconected came up}Replaced pair and took out other pair and 31 devices lost-sorry been a long day and need to close this one,
Reply
#4
If its a new build then you should know the cable route and short circuit isolators.
Start from beginning and go from device to device after first checking the led on the isolators.
Reply
#5
Humphrey Wrote:Hi i am an electrician,new to fire alarms as i said earlier i took out a pair from the panel and lost 9{devices dissconected came up}Replaced pair and took out other pair and 31 devices lost-sorry been a long day and need to close this one,

I'd be looking between (and including) the 9th and 10th device from the panel. The chances are its some kind of base/connection fault rather than a physicaly damaged cable. Unless there's plumbers been around!
Reply
#6
get me a gun
Reply
#7
With one side out you lose 9 devices; replace the pair & move to one of the devices that you lost & create an open circuit at this point. Return to the panel and note which of the original 9 are now not lost; continue this way until you create an O/C that doesnt lose anymore devices. Repeat for the 31 device side if you cant work out the next point on.
This is typical half way split. Should take more than a couple of hours max. It would speed up fault finding if you have an XP95 test set too, if field devices are far from the panel.
IFE Registered Fire Risk Assessor

www.ajfire.co.uk
01245 392014
Reply
#8
Thanks i will try that tommorrowCool
Reply
#9
Graeme Wrote:get me a gun

Got some Prozac.:P
http://awacsuk.com

advanced warning and communicated systems
installation...integration...innovation....

any comments or views posted are mine and I'm keeping them.
Reply
#10
Here endeth the lesson.
IFE Registered Fire Risk Assessor

www.ajfire.co.uk
01245 392014
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Sita 200 plus Short Circuit Leolion2177 12 493 24-05-2018, 07:13 PM
Last Post: Adi
  Static 900 fault codes Ilindley 8 428 06-04-2018, 12:47 PM
Last Post: Ilindley
  gcu fault on zp3 4loop panel christopher wasike 13 2,119 04-04-2018, 09:30 PM
Last Post: Adi
  Advanced loop card short circuit testing xenex100 60 19,795 06-03-2018, 10:07 PM
Last Post: Monkeh
  transparent fault on a morley zx5 alonso 4 913 14-10-2017, 11:47 PM
Last Post: sparky999
  morley network fault to a.r.c. alonso 11 2,654 07-09-2017, 02:20 PM
Last Post: sparky999
  Wiring open collector of fire panel gherasim 19 5,590 13-02-2017, 07:46 PM
Last Post: Monkeh
  low output vesda fault from vesda panel sammyunique 10 4,525 22-01-2017, 02:06 PM
Last Post: SergeTL
  Advanced MX4 Panel Fault Kennedy0121 7 3,369 08-12-2016, 06:39 PM
Last Post: Monkeh
  Morley ZX Panel 'COMP' Fault gillsman 8 3,961 31-07-2016, 07:15 AM
Last Post: bob1

Forum Jump:


Users browsing this thread: 1 Guest(s)