Positioning of Manual Callpoints
#1
Manual call points should be located on escape routes, at all exits to free air and at all exits from each level of multi-storey buildings.

For general applications, call points should be located such that nobody need to travel more than 45m to reach the nearest call point. This distance is based on measuring the actual route that would be travelled. If at the design stage the actual layout is unknown then a straight-line distance of 30m should be used as a design guide and the 45m limit verified after fit out is complete.

Call points should be located near to specific hazards (e.g. flammable liquid store) and at 1.4m (+/- 0.2m) from the floor in well lit easily accessible positions. Lower mounting heights might be needed to accommodate building users in wheel chairs.

The figures of 45m and 30m above should be reduced to 25m and 16m respectively if either a significant proportion of building users have limited mobility and it can reasonably be assumed that one of these occupants will be likely to be the first person to operate the alarm or if the nature of equipment or activity in an area gives a high likelihood of rapid fire development. The method of operation of call points should be the same throughout the building - all Cooper Lighting and Security call points meet this requirement, whether IP65 or standard types.

[Image: 712a.jpg]

[Image: 712bc.gif]

Typical building layout showing positioning of callpoints
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  adt minerva acpm 125-065-821 manual alonso 1 869 24-08-2018, 05:15 PM
Last Post: Kibeth
  manual required mo2 5 2,960 15-07-2017, 02:08 PM
Last Post: sacred
  Advanced Software Manual Clarkie 3 2,822 26-06-2017, 10:34 PM
Last Post: COMM ENGINEER
  callpoints in EX areas jk777 3 2,969 22-06-2016, 10:12 AM
Last Post: jk777
  Zettler Manual waring8953 2 4,041 20-06-2016, 07:47 PM
Last Post: waring8953
  KAC callpoints on Rafiki Twinflex Checkpoint Plus AnthonyB 7 5,613 20-03-2016, 06:53 PM
Last Post: saxondale
  ansul manual needed chris 7 9,207 01-03-2016, 11:05 PM
Last Post: SFSS
  Minerva Marine T1008 Fire Panel Manual needed contractor999 15 36,116 05-02-2014, 09:28 AM
Last Post: indiaszagalo
  Wormald fd-4 panel manual/repeaters alonso 0 2,481 18-03-2013, 01:16 PM
Last Post: alonso
  Guardall Beam Master Manual Required biker boy 9 12,414 31-01-2013, 11:41 AM
Last Post: Tilly

Forum Jump:


Users browsing this thread: 1 Guest(s)