most suitable type of detection for high condensation areas
#21
For the Hochiki weatherproof heats, I've used standard ip65 adaptable boxes in the past and just put the connections inside and mounted the base directly to the lid, haven't had an issue yet, although these are just under a canopy and aren't being subjected to washing down or high condensation.
Reply
#22
(06-03-2015, 08:47 PM)MD Martin Wrote: I'm intrigued to know where in EN54 it states that a sounder beacon is required to be a VAD Huh! To my knowledge (I may be wrong) that is not the case!

Isn't it CPR that specifies that devices must be EN54-23 approved.. A sounder must be a VAD, if it includes a light type element that doesn't comply as a VAD then it isn't a beacon for the purposes as a VAD its just a "visual Indicator" element. If Beacons are needed on site for noise or DDA reasons then they must comply.


Reply
#23
(09-04-2015, 11:23 PM)Digger Wrote:
(06-03-2015, 08:47 PM)MD Martin Wrote: I'm intrigued to know where in EN54 it states that a sounder beacon is required to be a VAD Huh! To my knowledge (I may be wrong) that is not the case!

Isn't it CPR that specifies that devices must be EN54-23 approved.. A sounder must be a VAD, if it includes a light type element that doesn't comply as a VAD then it isn't a beacon for the purposes as a VAD its just a "visual Indicator" element. If Beacons are needed on site for noise or DDA reasons then they must comply.

I think the key criteria for EN54 compliance is if the visual element is to be used as a 'primary' indicator (I'm not 100% though).
Found this...

http://www.vimpex.co.uk/download/vimpex-vad23.pdf
And this...

http://www.hochikieurope.com/ckfinder/us...287%29.pdf
One more...

http://www.ifsecglobal.com/en54-23-stand...-answered/
www.ajfire.co.uk

"Independent BAFE Accredited Fire Protection Specialists"

- SP203-1; FDA Maintenance; 
- SP205-1; Life Safety Fire Risk Assessment
- Members of the Fire Industry Association (FIA)
- SafeContractor Approved


Reply
#24
(27-02-2015, 09:38 AM)wozzer38 Wrote: Just a note, Apollo Marine are no more waterproof than standard detectors, they just have more approvals.
I would go with the Vesda if I had to make the choice.
Wozzer38 Apollo Tech

Sorry to bring a five year old thread up but Marine detectors, what extra approvals do they have?
Reply
#25
(16-09-2020, 07:44 AM)Trickle Charge Wrote:
(27-02-2015, 09:38 AM)wozzer38 Wrote: Just a note, Apollo Marine are no more waterproof than standard detectors, they just have more approvals.
I would go with the Vesda if I had to make the choice.
Wozzer38 Apollo Tech

Sorry to bring a five year old thread up but Marine detectors, what extra approvals do they have?

Maritime Coastguard Agency (MCA), Lloyds Register, Wheelmark....those types of approval so that they can be used on offshore applications. Detectors are exactly the same as standard devices though. They are for indoor areas on boats and ships and oilrigs etc.
Reply
#26
Thanks wozzer38. Speaking to a customer yesterday who told me he has had the existing conventional smoke detectors replaced with marine type due to condensation issues. So he’s basically wasted his money?
Reply
#27
Class, lol
Reply
#28
A little further reading and the only difference I have read is that the marine detectors have a fault LED?
Reply
#29
(17-09-2020, 04:55 AM)Trickle Charge Wrote: A little further reading and the only difference I have read is that the marine detectors have a fault LED?

No they don't, they are exactly the same as standard devices....yes he has wasted his money....but people only have to call us and ask....we don't mind people asking the questions.
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Fire Detection System Design Software Pro Metheus 0 1,125 16-06-2019, 04:37 PM
Last Post: Pro Metheus
  Natural Gas Detection mr ab 1 920 17-03-2019, 10:51 AM
Last Post: MW63
  ALM device type MW63 2 1,029 15-02-2019, 09:56 AM
Last Post: MW63
  VERY LOW (-42C) CABINET FIRE DETECTION Pro Metheus 1 881 11-12-2018, 11:52 PM
Last Post: Tilly
  Gent Nano change device type Bero 2 1,254 27-11-2018, 11:17 AM
Last Post: Bero
  CO Detection kevinhynes 3 1,712 09-10-2018, 05:34 PM
Last Post: Tilly
  High resistance loop advanced mx pro 5 dcarney 18 9,148 05-05-2018, 09:09 PM
Last Post: Monkeh
  callpoints in EX areas jk777 3 3,331 22-06-2016, 10:12 AM
Last Post: jk777
  Advanced mx4100 charger too high fault Bero 3 3,368 05-02-2015, 09:02 PM
Last Post: cctvfitter
  Suitable replacement fire panel andyfire 18 14,520 23-04-2013, 09:18 PM
Last Post: ESP

Forum Jump:


Users browsing this thread: 1 Guest(s)